In Topic: Frozen Rowe 548

28 July 2010 - 06:24 PM

I believe the problem has be corrected. Had the refrigeration guy, no relation to the cable guy, pull the unit and bench test it. During the testing process he felt the evaporator fan was not turning fast enough. Fan was replaced about 6 months ago with a new unit. He replaced the fan, benched the unit and reinstalled. The machine has run properly for the last 10 days and I am confident the problem has been corrected. Thanks for all you help. Hope I can return the favor.

In Topic: Frozen Rowe 548

21 July 2010 - 09:07 PM

Thanks for the input. Turned master switch off for three days, unit did totally deforts. You are correct regarding the warm enviroment. A/C is controlled via a computer system elsewhere. Turns off for about 6-8 hours in the break room after the completion of one shift and beginning of the next at mid-night. I will check the seals, especially the main door seal and make sure the machine is as least 6 inches from the rear and side walls.

In Topic: Frozen Rowe 548

21 July 2010 - 08:55 PM

if it is a new unit.....and it itself is pulling a good frostline......sounds to me that you are sucking a lot of hot humid air from somewhere.....check the seals around the duct where it flows cold air into the cabinet, your main door seal...is machine at least 6 inches from wall to allow compressor to breathe/exhaust air?

if the unit is new, you can bench test it.....pull it out, apply 110volts to the unit, block evaporator fan,.........in a few minutes frost should appear "evenly" thru out the condensor....if partial....could indicate low charge........

also if you been fighting this very long...you could have ice built up on the condensor, which even tho you think you have completely defrosted it, it may not be.....

by pulling slowly to 45.....i still suspect gasket leaks pulling in hot air.......is it in a very hot place?.......rowe"s at initial start up should makw health timer very close to one cycle......

In Topic: Rowe 548 Cold Food Machine

16 July 2010 - 08:33 PM

New to the group, but, before turning off the main power switch rotate the turntable from the inside of the main door. Also make sure the vending doors are completly shut. Whenever I turn off the main power switch I must also "rotate to zero positive."